Hi, basically you are right. Here the answeres to your questions: 1. The setoint for the PID is dataformat REAL. 2. If you trasfere a word from the HMI then the answere is YES because the Setpoint for the PID requires a REAL. 3. Yes in nearly all PID applications you need to scall and in lots of other applications also. 4. I have seen "NAN" in the past if the value is a REAL and in the status chart you selet a DWord. This I never had since an update to MW V4.0 SP6. Here is a link where you can download a scalling library for free: http://support.automation.siemens.com/WW/view/de/27043396 I hope this helps. Regards Helmut |