4/24/2019 3:32 PM | |
Joined: 11/8/2017 Last visit: 7/16/2024 Posts: 328 Rating:
Hi, The log data you see in Object Viewer comes from within the PX, i.e. what you are seeing is the log. Sorry, but I'm not aware of there being any other log that's available to be viewed. Is this the same PX that we discussed here? ---> Intermittent communication errors with the PXCs I was under the impression that the PX that was rebooting was a PXC64-U. Regards, |
This contribution was helpful to
1 thankful Users |
4/25/2019 3:57 PM | |
Posts: 17 Rating:
It sounds like we have been misinformed :-) |
4/27/2019 1:17 PM | |
Hi, The Diagnostics info for a PX can be viewed using 3 different methods.... 1. Using Object Viewer in Desigo Insight / CC. 2. Connecting via XWP > Online Properties > Diagnostics. 3. Using the Desigo Firmware Download Tool > Diagnosis. The Diagnostics info is the same, regardless of the method you use to find it. Using the Desigo Firmware Download Tool, I attach a dump file as an example that has come from a PXC36.D. Regards, AttachmentDiag_PXC36-D_27-04-19_1205.txt (329 Downloads) |