9/24/2008 2:55 PM | |
Posts: 38 Rating: (0) |
Hello All, is there a possibility to connect CPU S5-115U to S7-200? Thanks in advance for any hints, Petr |
9/24/2008 4:32 PM | |
Posts: 487 Rating: (45) |
Easiest way is using profibus-DP. In 115U you need to use IM308C as DP master and EM277 in S7-200 as DP slave. |
10/9/2008 2:41 PM | |
Posts: 487 Rating: (45) |
I have used IM308C and EM277 separately, but nto together in one project. But I do not think there is any problem. |