Joined: 5/6/2010 Last visit: 9/21/2024 Posts: 1978 Rating: (276) |
Hello, how do you configure your F-module ? I there a working/programmed F-function? regards |
5/8/2019 11:08 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
hi geri036, when there is no output used in the F-program, the outputs are not written from the process-image to the modules. You have to use at least one variable in your F-program.
But when you use your outputs in your F-program and controll this outputs from HMI, your CPU will go into Stop beause of"Data corruption in the safety program ..." I recommend you to use normal periphery, when you don´t want to use F-modules. hope this helps, regards, |
FCK WAR! |
|
5/8/2019 11:30 AM | |
Posts: 152 Rating: (5) |
Thnaks! |