Dear All, I am Using S7-1214 c dc/dc/dc & TP900 Hmi, I want Time Synchronization between plc to hmi as Plc is Consider As a Master & Hmi Consider As slave. I have Configured Hmi As a Slave From Connection & It works when communication Cable removed Or Recycle My Hmi & Again Reconnect the Cable Then Time is Update With Plc. But now I want to Update Hmi Tp900 System Time Automatically For Every Hour or every day. I Have Checked All the Possibilities But I dint Get success, Please Suggest If You Have Any Idea Related To this Thanks In Advanced. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 05/13/2019 06:37:10New subject after splitting |
|
5/13/2019 12:49 PM | |
Joined: 8/3/2009 Last visit: 11/19/2024 Posts: 14206 Rating: (1775)
|
Hello vicky bhau as we can read in here: https://support.industry.siemens.com/cs/ww/en/view/69864408 If you use the Slave setting in the HMI Connection then the Time is been synchronized at Connections establishing and every 10 minutes. If you want to set the cycle for you own you can use Area Pointer for this Task. But never use Area Pointer and the setting in the Conneciton for tyme synchronisation together. This will cause always errors. Bye Murof |