1/8/2014 6:16 AM | |
Joined: 1/2/2014 Last visit: 5/24/2024 Posts: 142 Rating: (22) |
Dear Experts,. How to confgiure the ATM 60 encoder for working as a slave under s7 315. Shall I am able to read n write using SFC14/15? I got the GSDfile. While putting it in the Hardware configuration what should I enter n the paramaters? Some hexadecimal values are there to be entered. Have any one configured with simatic manager please help me out. the memory mapping of ATM 60 is not understanding to me. I am attatching theProfibus_encoder_connection.pdf
AttachmentProfibus_encoder_connection.pdf (706 Downloads) |
1/8/2014 1:03 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (714) |
Hello, If your CPu is a 315 2dp, there is no need to use FC14/15. Follow the steps as shown in attached document. Pay attention to the profibus speed and adress of your Encoder. Regards, Marcjan AttachmentSick_encoder.pdf (767 Downloads) |
Problem solved? |
This contribution was helpful to1 thankful Users |
3/22/2014 10:08 PM | |
Posts: 13 Rating: (0) |
I think that use a counter as a divisor or something like that should be fine. I'm not expert, but that is the most inmediate thing I would do using step 7. |
6/15/2019 5:00 PM | |
Joined: 4/14/2010 Last visit: 5/14/2024 Posts: 525 Rating: (11) |
AttachmentAbsolute Encoder Example.zip (276 Downloads) |
MS |