Hello Hero_pro, the PIDConL block doesn't support a function to inhibit the increase of MV. The PIDConL block has the Inputs "IntHoldPos" and "IntHoldNeg" with the Parameter "1" the Integrator cannot run in positive/negativ direction (see the manual Advanced Process Library in the section PIDConL I/Os). This method is used against the integrator windup for cascade control within the distributed control system (see the templates of the PCS 7 Advanced Process Library). Another solution is to implement this function in a CFC. In the attachment you can find an example CFC to inhibit the increase of MV. The blocks have following function:
With regards |
7/16/2019 10:24 AM | |
Joined: 12/12/2011 Last visit: 9/17/2024 Posts: 69 Rating: (1) |
Hello Heisenberg2, Much Appreciated your help?? Thank you Heisenberg2 very much |