I am using a 3RT1064-6AF36 contactor and I am wondering how many cable lugs can I connect to the connecting bar on the contactor? |
10/10/2019 8:49 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (878) |
3RT1064-6AF36 contactor rating at AC3 - is 225 A. You may connect n number of lug to its busbar connection but total load current per pole should not exceed 225 A (400 - 690 Volt) @ AC-3 load cycle. (refer technical data) HTH |
Last edited by: PISCEAN 2010 at: 10/10/2019 08:51:42technical data sheet added |
|