Hi,
It sounds that somthing for the upgrade procedure wasn't done. Did you follow the guide "PCS 7 Software update without utilization of new functions for PCS 7 V9.0..." In e.g. did you run the 'OS Project Editor'. This is important to renew the system PDLs.
Do you know the script diagnosis? Can you open it and watch what it says when clicking?
Again I'm more confused... Are the custom faceplates use own @PG_APL_OA....PDLs.? Usually there are only three types of @PG_APL_OA....PDLs. The same @PG_APL_OA....PDL is used by different blocks (their faceplates). I expected the custom faceplate to use the same @PG_APL_OA....PDLs. You see, there is a lot of potential for missunderstanding and also a lot of things to analyze. I'm afraid we will not come forward this way...
Problem with standard blocks or not? Also one problem is a problem...'most of it' is fuzzy...
You can not leave out the conversion of CFC. It is a 'must do' ! Updating the blocks is an own topic and independant of converting the charts to the current version of CFC.
See my pervious post.
Maybe you can use PLCSIM together with WinCC.... |
"Expert" does not necessarily mean Siemens employee. Please cross-check your requirements always with official Siemens documentation. Also "Experts" are pleased about feedback. Please don't send support requests as PM. Questioners who don't follow up their thread will be put to my list of users to be ignored. |
|