2/19/2020 12:36 PM | |
Joined: 5/12/2006 Last visit: 11/13/2024 Posts: 22449 Rating: (3029) |
hi, this HSP is for TIA Portal V15.1 ore above and can not be used with V12! Regards |
2/20/2020 7:05 AM | |
Joined: 5/12/2006 Last visit: 11/13/2024 Posts: 22449 Rating: (3029) |
Hi, from the Release informations of PLC: Compatibility of the Hardware and Software AnS7-1200 CPU V4.0 is (spare-parts-) incompatible with anS7-1200 of Firmware V3.0. An existing S7-1200 project, created for Firmware V3.0, can continue to be used on a CPU V4 after compiling the project (error-free) with the engineering system STEP 7Basic / Professional from V13. from the Release information of modules: The innovated signal modules (6ES7 2xx-xxx32-0XB0) replace the previous signal modules (6ES7 2xx-xxx30-0XB0) and are spare-parts-compatible with them. The revised modules can be used without changes in place of the previous signal modules. so yes is possible to use the modules with V13. You create a config with thew older modules and download it to the PLC.
Christoph |
This contribution was helpful to1 thankful Users |