7/7/2020 4:49 PM | |
Joined: 2/1/2010 Last visit: 5/14/2024 Posts: 136 Rating: (68) |
Route Control is not compatible with Multiple Single Station OS, unless only 1 of the single station will have RC (which doesn't seem to make sense). According to the RC manual Single station redundant may be supported, but this might just be a nuance of the document trying to show how you can do 2 redundant servers with OS/RC/BT all on the nodes. Doing single station redundant with RC would be a very unusual edge case, and I don't think that is a reasonable solution for you anyhow since you would still have to OS without RC available. (Single station can't be RC clients.) In short: You need to move to server/client architecture if you want more than 1 OS station with RC capability. Route Control Manual - see chapter 5.4 https://support.industry.siemens.com/cs/ww/de/view/109755006 |
Last edited by: Jen_Moderator at: 07/08/2020 08:41:35Optimized link. If my post helped you, please rate. Thanks. |
This contribution was helpful to1 thankful Users |
Follow us on