Where are the data areas viewed that are assigned when configuring a telegram? I am just learning to program Siemens and am looking at existing programs using TIA Portal Prof. v14. The G120C drives all have telegrams configured and there are "Partner Data Area" assignments like: I 156...161 Q 156...161 I 1036...103 Q 1036...1059 The partner is the CPU (1512SP F-1 PN). Where can I look at a table similar to that of the assignment list that will show these areas? Thanks! ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 10/15/2018 7:41:01 AMNew subject after splitting |
|
10/15/2018 8:39 PM | |
Posts: 4 Rating: (0) |
Okay, I figured it out! Devices & Networks > Click the PLC (CPU) > General Tab > Overview of addresses Now, I can see all the addresses mapped to the PLC! |