1/26/2018 6:08 AM | |
Posts: 1 Rating: (0) |
Hello every one, I'm a beginner in PLC. I just get a 1214C AC/DC/Relay. I connect it to my LAN port but in TIA13 didn't find any accessible node. The all three LED of the PLC are blinking and never stops. I ping the address 192.168.0.1 and its ok. I'm using windows 10, and didn't have any MC in the PLC. Please help me.. Thanks in Advance ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 1/26/2018 7:50:32 AMNew subject after splitting |
|
1/26/2018 7:37 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi xubaer, What PLC do you have exactly? Which SW do you use? Step7 Vxx? Three blinking LED normally means the PLC is defect, or an error in the FW. The LED-blinking-codes are described in the manual, chapter 15.
SIMATIC S7 S7-1200 Programmable controller hope this helps, regards, |
FCK WAR! |
|