11/27/2017 2:39 PM | |
Posts: 6 Rating: (0) |
I have revised my topic to convert 0-20mA to 0-10VDC. The 1215c Analog outputs can only be configured as 0-20mA, no other options are available. Thanks, John |
11/27/2017 8:05 PM | |
Posts: 6 Rating: (0) |
Yes, 2M is connected to the common of the system (this is also tied to M and 1M at different parts of the PLC). Thanks! |
11/27/2017 8:07 PM | |
Posts: 6 Rating: (0) |
Good call. I tried a 480Ω resistor across 2M and AQ1 terminals with no change. Across 2M and AQ1 is 0VDC. kind regards, John |
11/28/2017 7:38 PM | |
Posts: 1529 Rating: (202) |
If you are always getting 0V, then 1. You are writing to the wrong output word 2. You still have a wiring problem 3. You broke it. |