hi Kragnz. In my opinion, the easiest way is to establish an IDevice-communication. One of the CPU is an IO-controller and the other two are connected over Profinet as IO-device. They are communicating over the cyclic IO. See this application sample and manual: Configuration and application of PROFINET I-Device function SIMATIC NET: PROFINET I-device user programming interface You can also establish S7-connections between the CPUs and make the communication over PUT/GET. there is also an application sample.(The IM151 is working like a S7-300) Application for the "PUT" and "GET" Function Blocks of the S7 Communication hope this helps, regards, |