Hi, You can increase the block range of FC's and DB's via the following: 1. Open a CFC chart 2. Go to Options->Customize->Compile/Download and in the menu you can adjust the range. 3. Afterwards you need to use the "Compress" option. But, this involves the following: - You need to execute a full download - Readback is not possible anymore, only when a full download is executed. The FB range is limited by the CPU you are using. Certain CPU416's can only use FB ranges up to 2048. If higher, download is not possible. A CPU417 or 410 can have ranges up to 8000, with a maximum of 5000 FB's in a CPU. You can use the MLFB number of your CPU to get the technical data sheet from Siemens and check what the limit is of the FB's. Good luck! |