12/13/2015 4:28 PM | |
Joined: 10/14/2009 Last visit: 10/17/2022 Posts: 140 Rating:
|
Hello everybody I have CPU S7-300-2DP-PN , AI "331-7KF02-OABO" AND ABB DRIVE AC880 I WANT TO WATCH ITS SPEED ON HMI AFTER CHECK THE DRIVE OP IT 0-20mA AT AI MODULE IF I CHOOSED 2 WIRES NO OPTION FOR 0-20 ONLY 4-20 IF I CHOOSED 4 WIRES THERE IS 0-20 MA OPTION AND DRIVE IS TWO WIRES. if i choosed 4 wire return value of fc105 is 8 PLEASE CHECK ATTACHED Any one can help??
AttachmentOUT CARD.rar (213 Downloads) |
12/13/2015 10:02 PM | |
Joined: 3/30/2011 Last visit: 6/1/2023 Posts: 731 Rating:
|
Hello, 2 wire means power supply and signal in the same 2 wire, 4 wire means 2 wire only for signal and power supply from other connection. In your case you have to put 4 wire in hardware configuration. Your analog input board also have range module. Please check if you have correct wiring and correct module position at pag.372-373 of this manual.
|
★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★ |
|
This contribution was helpful to
3 thankful Users |
12/14/2015 6:31 AM | |
Joined: 1/21/2013 Last visit: 4/21/2023 Posts: 4617 Rating:
|
Hello Sherief, I addition to our friend mindware: S7-300 SM331; AI 8x12 Bit Getting Started part 1 ... - SiemeFC 105 with RET_VAL W#16#0008 mean that your input value in greater than 27648 or less than 0Scaling and Unscaling Analog Values - Siemens |
This contribution was helpful to
1 thankful Users |
12/14/2015 7:31 AM | |
Joined: 10/14/2009 Last visit: 10/17/2022 Posts: 140 Rating:
|
thanks ste39 you r right, in attached you will find PIW is 32767. |