12/24/2019 5:28 PM | |
Joined: 5/6/2010 Last visit: 9/21/2024 Posts: 1978 Rating: (276) |
Hello, so far I know do you need for G-commands a T-CPU, Please look at this Link - Handling with SIMATIC S7-1500 T-CPU Maybe is this helpful for your application. regards |
This contribution was helpful to1 thankful Users |
12/26/2019 6:20 PM | |
Joined: 2/9/2015 Last visit: 6/6/2024 Posts: 65 Rating: (1) |
thank you so much but already we have ET200SP cpu and we can not change it i have to use it |
1/9/2020 10:49 AM | |
Joined: 4/28/2015 Last visit: 9/20/2024 Posts: 397 Rating: (56)
|
Hello, please have a look to the documentation of the following application example:
I know, it is made for S7-300T, but maybe it will show you the principle to "translate" G-Code to PLCopen motion contol functions, like G0/G1 -> MC_MoveAbsolute (S7-1200/S7-1500(T) without kinematics) or MC_MoveLinear (S7-1500T with kinematics). |
Follow us on