Hello JRubio; You cannot use the integrated port of the CPU 315-2DP to process S7 communication blocks or connections. This is a feature of the CP 342-5 only, as it support S7 communications. The integrated port of a CPU (either MPI or Profibus) only supports S7 basic communications. The links below are a source of information on the subject.. If your MPI ports are available you can use them to connect the CPUs over S7 connections, using X_PUT/X_GET or X_SEND/X_RCV blocks. This FAQ can provide details: Options for communication over MPI: https://support.industry.siemens.com/cs/ww/en/view/21537047 There are many discussions on the forum on that subject, I can point this one out for you: https://support.industry.siemens.com/tf/ww/en/posts/28684/ Follow the suggested link in that thread for information on data exchanges between CPUs. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 11/23/2015 3:32:58 AM |
|
This contribution was helpful to
1 thankful Users |
11/25/2015 8:23 AM | |
Joined: 10/7/2005 Last visit: 3/27/2025 Posts: 3043 Rating:
|
You are indeed spot on correct dear jrubio34 an good on you for persisting and working this out. I suggest you grab a copy of the CPU-CPU Communication with SIMATIC controllers which also confirms that what you are doing is correct in this case and will come in handy in the future when trying to work out what can and what can not be done. |