8/25/2014 10:15 PM | |||||
Joined: 9/27/2006 Last visit: 9/21/2024 Posts: 12282 Rating: (2684) |
Hello Dreni; This CPU does not have an integrated Profibus-DP port; you must use a CP 342-5 to enable connection to a DP network, as master or slave:
Look at this collection of FAQs for sample projects: What master/slave communication options are available on PROFIBUS DP? Study the example with a S7-300/CP 342-5 (as master) to a CP 315-2DP (as slave) to serve as a basis for your project; select the proper slave CPU for your configuration.. Hope this helps, Daniel Chartier |
||||
This contribution was helpful to2 thankful Users |
8/26/2014 1:34 AM | |
Posts: 9 Rating: (0) |
Thanks for your enlightenment!! I really appreciate it. Regards, Dreni
|
Follow us on