5/9/2014 2:59 PM | |
Posts: 467 Rating: (59)
|
hello DocT, it's the conductor capacitance that causes the above mentioned behaviour. The attached report describes this subject. The also attached catalog page shows a 3RT1916-1GA00 ''additional-load'' module. This module contains a resistor 22 kiloOhm and can be plugged into a 3RH1122-1AP00 contactor relay. Not knowing the actual conductor capacitance we are unable to guarantee that this accessory will help, but there is a good chance that it does. AttachmentD:\report on long cable runs.pdf (257 Downloads) |
This contribution was helpful to1 thankful Users |
5/9/2014 3:03 PM | |
Posts: 467 Rating: (59)
|
kind regards LesPaul AttachmentD:\catalog page.pdf (228 Downloads) |