2/18/2013 9:06 AM | |
Posts: 467 Rating:
|
Hello, basically it is not according to the safety rules 'only'to switch off the power supply of the relay outputs. We have shown various examples for safety shut-down in or manual of the latest Simocode generation 3UF7 (attached you will find the example for Direct-starter with safety Category 2 ). Toavoid a general fault tripping of Simocode you have to give in case of emergency stop an additional 'normal' off-signal tom Simocode e.g. via the Hardware-inputs.
best regards LesPaul AttachmentD:\3UF7_System-Manual_SIMOCODE pro_ 2007-03_en.pdf (263 Downloads) |