Hi, Can we connect 4 -300CPU in profinet communication? Is it mandatory to go with PN/PN coupler and CP cards? |
3/13/2017 1:21 PM | |
Joined: 7/9/2015 Last visit: 3/21/2025 Posts: 4203 Rating:
|
Hi, no, it´s not necessary to use CP/Coupler. You can use the integrated PN-Interface of the PLC (if there is only DP/MPI, you need a CP). Please check the following manual: CPU-CPU communication with SIMATIC controllers (compendium)On page 95 you will find some informations how to communicate between S7-300. Regards, Towome |
|
|