Hello,
Eng.Mohamed Ibrahim |
This contribution was helpful to
1 thankful Users |
11/2/2020 2:40 PM |
Joined: 7/7/2010 Last visit: 9/25/2023 Posts: 13721 Rating:
Last edited by: 0_Einstein at: 11/02/2020 22:57:51correction - my prior post was *wrong* science guy |
11/2/2020 6:13 PM | |
Hello, Please have a look at the attached photo. The 4-wires transmitter is an active 4-20mA output. The 2- wires analog input module is an active module. You can't install 2 active components directly in the loop. You need to install the Isolator with passive(sink) output between 4-wires transmitter and 2- wires analog input module. |
11/28/2022 1:18 PM | |
Joined: 6/19/2017 Last visit: 9/25/2023 Posts: 7293 Rating:
New question published by Booleans is split to a separate thread with the subject Which type of Isolator can be used ?. Best regards |