Hello everyone; There are 4 servo S210 and there is a D425-2 DP/PN CPU on my system. Also there is an external encoder. The problem is ''after system is started, it stops randomly, sometimes at the first application (layer) sometimes on the middle layer or at the last layer and the system gave 40005 and 20005 error with others. (There is no DP communication on the system)(Sometimes only 20005 error) (Added the some code there might be a problem) Tia Portal Diagnostic AttachmentDevice Diagnostics_Simotion.txt (672 Downloads) |
Last edited by: Deep1nside at: 04/04/2023 10:01:40Last edited by: Deep1nside at: 04/04/2023 10:06:21 |
|
4/5/2023 9:09 AM | |
Joined: 10/11/2006 Last visit: 4/24/2025 Posts: 6009 Rating:
|
Hello, when drive/encoder or communication is not ready, or there are communication failures, TO axis is not enabled or loose enabled status. There is a application for start up. SIMOTION Startup Checkhttps://support.industry.siemens.com/cs/ww/en/view/48947625 During operation reason could be: Drive does Safety functions, like STO. There are communication failuers. Please check quality of profinet cables - Wiring - What Hubs do you use(IRT) - EMV-problems? |
With best regards, |
|
This contribution was helpful to
1 thankful Users |
4/5/2023 11:23 AM | |
Joined: 10/11/2006 Last visit: 4/24/2025 Posts: 6009 Rating:
|
Hello, 20005 is the reason for 40005. Check the manual for complete explanation. https://support.industry.siemens.com/cs/ww/en/view/109801487 |