11/23/2017 12:37 AM | |
Posts: 305 Rating:
|
does 414-5H can via profinet-io connect et200m ,running at redundancy?redundancy is two cpu menage io and db 、m data ,not io redundancy connect。 |
11/23/2017 2:39 AM | |
Joined: 9/27/2006 Last visit: 3/17/2025 Posts: 12344 Rating:
|
Hello TechWing; You can connect redundant S7-400H CPUs with distributed I/O stations (ET 200M) over Profinet. See the following document: https://support.industry.siemens.com/cs/fr/en/view/66644434 Redundancy with S7-400H systems is 2 CPUs linked with fiber-optic links for very fast transfer of data (and programs) between the master and stanby CPUs, to mange all relevant data, including redundant connection of I/Os. Please doiwnload and study the following manual for all the details:
https://support.industry.siemens.com/cs/fr/en/view/82478488 Hope this helps, Daniel Chartier |
Last edited by: Jen_Moderator at: 11/23/2017 11:10:03 AMInserted right links. |
|