2/19/2015 5:36 PM | |
Joined: 11/29/2011 Last visit: 5/7/2024 Posts: 1358 Rating: (229) |
Hi, No problem. Have a look at this link about diagnosing Profibus networks: https://support.industry.siemens.com/tf/ww/en/posts/19855/ By the way my favorite method is the visual inspection. Most of the cases the issue caused by a broken plug, loose wire, injured cable ... and POWER SUPPLY... This can be found by a good pair of eyes!
- What you read here, please check with manuals and your requirements. |
2/20/2015 11:46 AM | |
Posts: 21 Rating: (0) |
Hello Thanks microman Today we conducted testing of profibus communication by using profibus tester (Profi-TM Professional) during the testing it shows a good communication signal, i attached the recent diagnostic buffer i extracted in reference with the alarm happen recently. I suspected that it is lose its communication suddenly that is why there is an access error recorder and at the event 69 it stop already. I will check all the profibus connector and cables for visual problem and will update you again regarding the problem. Thanks AttachmentDiagnose1.rar (155 Downloads) |
2/20/2015 5:03 PM | |
Hi, I think we have got it! Great work there! By the there is a good FAQ about your problem: STOP through the priority class run system |
Last edited by: MicroMan at: 2/20/2015 5:06:09 PM- What you read here, please check with manuals and your requirements. |
3/26/2015 1:03 PM | |
Here is the diagram of the network |
3/26/2015 1:04 PM | |
The profibus properties |