9/18/2014 7:40 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715) |
Hello, Check your settings with help of the attached part of manual. Regards, Marcjan Attachment466-3LA11.pdf (388 Downloads) |
Problem solved? |
|
9/18/2014 7:44 AM | |
Joined: 4/5/2006 Last visit: 8/13/2023 Posts: 642 Rating: (131) |
Hello, the 466-3LA11 has no measuring range sub modules! Have you checked all DIP switsches? S1, S2, S5, S6, S7, S8, S9. Regards André Räppel --------------------------------------------------------------------------------- www.raeppel.de
work faster withinnovative PLC-Tools |
9/18/2014 8:38 AM | |
Posts: 5 Rating: (0) |
Thanx for your reply. I checked all the switches, here are the settings which I use for your review and further advice: S1 xx xx xx xx S2 xxxx xx xx S5 most Right S6 Left S7 most Right S8 Left S9 (First Module-Near CPU) xxxxxx xxx S9(Second Module-Right to the First Module) xxxxx x x x x Check the configuration and advice me if I missed any. Thanks ahead. Regards, |
This contribution was helpful to1 thankful Users |
9/18/2014 9:37 AM | |
Joined: 4/5/2006 Last visit: 8/13/2023 Posts: 642 Rating: (131) |
Hello, it looks good. Can you send pictures from original and new card dip settings? Regards André Räppel --------------------------------------------------------------------------------- www.raeppel.de
work faster withinnovative PLC-Tools |
This contribution was helpful to1 thankful Users |