7/16/2012 4:09 AM | |
Joined: 8/20/2009 Last visit: 12/14/2022 Posts: 80 Rating:
Dear VD1, I hope you have parametertized the Analog IOs in Hardware Configuration console as per your requirements. i.e., Selecting channels as Voltage inputs, 0-10 vdc. (As you also might be knowing that integrated Analog IOs have voltage range of +/-10 vdc.) I hope you are using Analog IO address as per Hardware configuration!!!! Also find the link from where you can download the manual for your CPU and you will also find the integrated IO wiring diagram inside on page 277. http://support.automation.siemens.com/WW/view/en/12996906 or else download this "SIMATIC S7-300 CPU 31xC and CPU 31x: Technical specifications" manual from automation.siemens.com. or else find the attachement of the page 277. I hope you will find the way. Vishp. AttachmentCPU314C-2 AI-AO connections.pdf (1878 Downloads) |
5/27/2020 12:09 PM | |
Joined: 10/22/2019 Last visit: 8/28/2023 Posts: 45 Rating:
hei Wishme,it means that i need to put 24v to pin 1 and 0v to pin 20.i cand get out my plc from SF.and in diagonistic buffer i see an error of that |