Dear pigroplc, as far as i know, the DI card 6ES7521-1BH00-0AB0 can not be used in combination with a "technology object" as this card is a "normal" peripherie, not dedicated a "technology module". This card has to be used via the control interface / feedback interface like described in the manual. Address space Counting modeExamples of countingStructure of the parameter data records Counting mode****EDIT**** This is also stated in manual above. "You control the counting function via the IO addresses of the module. These IO addresses are also known as the control interface (output addresses) and feedback interface (input addresses), see section ." SIMATIC S7-1500/ET 200MP Digital Input Module DI 16x24VDC HF -> Countregards sancruz |
Last edited by: sancruz at: 09/01/2022 04:54:05Feedback appreciated, please rate |
|
This contribution was helpful to2 thankful Users |
9/1/2022 5:40 AM | |
Joined: 4/3/2008 Last visit: 4/22/2024 Posts: 385 Rating: (16) |
Sancruz thanks for your accurate explanation. pigroplc |