Hello, You did forget about the PLC Cycle time. PLC reads inputs--- does the trick in the program--- sets outputs and then goes back to reading the inputs. You are missing counts because off that. If your module supports it: What is a hardware interrupt and how do they work in the S7-300 system? Regards, Marcjan |
Last edited by: Marcjan at: 9/23/2013 5:20 PMProblem solved? |
|
9/23/2013 6:04 PM | |
Posts: 4 Rating: (0) |
Hi, Just look in isochronous mode...seem i t only work on DP module any else recomendation ? Thanks |