4/16/2015 9:00 AM | |
Posts: 38 Rating: (0) |
Hello Experts, we have on 6RA7097-4KS22 mill stand drive, when we measure drive incoming R, Y, B current there is 100 amp difference between two phases, R=860, Y=810, B=920 Amp, (we measure this because we are observing problem in its incoming transformer 11kv/700v primary tripped once) i have attached this drive Trace-2 file, pls check and tell all thyristor are firing properly, how to check all THYRISTOR Firing properly ? (which is better P830 or U840 -give further idea on this) if one thyristor will not fire what is symptoms (what type of problem will occur). Thanks & Regards, Meet Attachmenttrace2.zip (286 Downloads) |
4/17/2015 7:59 AM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
Hello Meet You can Run Thyristor check using Control Word P830 = 3 However please note the conditions underwhich this can be done. You can also Manually check the healthiness of the thyristors as described in the following FAQ : https://support.industry.siemens.com/cs/in/en/view/50575033 Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
4/27/2015 1:17 PM | |
Posts: 38 Rating: (0) |
Thanks Navang & Vijay, we have check thyristor test and its details as attached document (6RA70 Thyristor doubt.pdf) , in addition i have attached (6RA70 FIRING.pdf), where we can see this problematic drive Current six pulse is not similar as normal drive. we have changed CUD-1, Power interface etc, please guide further what can be done. Regards, Meet Attachment6RA70 Thyristor firing problem.zip (384 Downloads) |