11/30/2013 12:15 PM | |
Joined: 8/25/2006 Last visit: 12/2/2024 Posts: 2211 Rating: (280) |
Hello. What was the fault value of F600052 (look at r0949)? Did you enable field-weakening in P50081?
|
6/5/2014 5:23 AM | |
Posts: 28 Rating: (0) |
i have the same problem, i can't run p50051 = 27 so we need feedback control to run this mode? |
6/5/2014 9:06 AM | |
Joined: 8/25/2006 Last visit: 12/2/2024 Posts: 2211 Rating: (280) |
Hello. When you are using field weakening mode you always need speed feedback from encoder or tacho.
|
6/5/2014 11:19 AM | |
Posts: 28 Rating: (0) |
hello KSN thanks for reply i convert to DC master to Sinamis DCM so i need to optimization Driver all mode or need to one option? this is file of parameter old driver AttachmentMASTER_tmpchane.zip (605 Downloads) |