Hello. You will needOperating Instructions,List manual. Also look for application manuals that is suitable for you:
|
12/16/2014 10:18 AM | |
Joined: 8/25/2006 Last visit: 12/11/2024 Posts: 2211 Rating: (280) |
Hello. What value has fault F60056, look in r949 while fault is active.
|
12/16/2014 10:38 AM | |
Joined: 8/19/2013 Last visit: 10/5/2024 Posts: 13 Rating: (0) |
r949 value is 9 when fault f60056 occurs.please help |
12/16/2014 10:41 AM | |
Joined: 8/25/2006 Last visit: 12/11/2024 Posts: 2211 Rating: (280) |
9: Reference speed (p2000) not set (factory setting value must be modified)! |
12/16/2014 10:55 AM | |
Joined: 8/19/2013 Last visit: 10/5/2024 Posts: 13 Rating: (0) |
But p2000 is not accessible even in expert list what to do |
12/16/2014 11:16 AM | |
Joined: 8/25/2006 Last visit: 12/11/2024 Posts: 2211 Rating: (280) |
On which drive object you try to look for p2000? This parameter is in Drive, not in CU.
|
12/16/2014 11:30 AM | |
Joined: 8/19/2013 Last visit: 10/5/2024 Posts: 13 Rating: (0) |
checking in drive object 1 and 2 both.... |