Help!!!!!! I have the 6RA80 dcm with the same problem F08501 when we have coms loss. i do not need this fault stopping operation for the propulsion motors. we are not using the profi net for control at all only for monitoring information. tried masking with 2100 and 2101 without luck. How can i mask this fault successfully? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 7/27/2017 2:15:06 PMNew subject after splitting |
|
7/27/2017 2:44 PM | |
Joined: 8/25/2006 Last visit: 12/2/2024 Posts: 2211 Rating: (280) |
Hello. Try to use p2118 and p2119. |
11/10/2017 3:30 PM | |
Joined: 9/1/2005 Last visit: 12/5/2024 Posts: 4114 Rating: (195) |
New question published by ANSHUMAN_SINGH is split to a separate thread with the subject G120C PROFINET vfd - how to mask F8501 fault. Best regards |