12/19/2017 6:15 AM | |
Posts: 57 Rating: (0) |
sir we are commissioning new Siemens 6ra80 drive.as per operation manual startup procedure as per Quick commissioning DCM 6RA80Created by:lsierdsmaat: 1/6/2015 11:03 AM (1 Replies).I am not getting acess autorisation parameter p0003.i did the parameterization as per process and p3900 made=3, but after that p0010 no gatting 0.also drive tripping on F60056.please guide the same. |
12/19/2017 6:54 AM | |
Joined: 8/25/2006 Last visit: 12/2/2024 Posts: 2211 Rating: (280) |
r0949 in 6RA80 contains fault value as in 6Ra70. You can also look in r50047[0]. |
12/19/2017 7:10 AM | |
Posts: 57 Rating: (0) |
R 50047 showing 3 |
12/19/2017 7:17 AM | |
Joined: 8/25/2006 Last visit: 12/2/2024 Posts: 2211 Rating: (280) |
3: Rated field current of the motor not set (p50102) |
12/19/2017 7:50 AM | |
Joined: 8/25/2006 Last visit: 12/2/2024 Posts: 2211 Rating: (280) |
List Manual with fault description. Operating Instructions, look for comissioning steps in chapter 8. |