12/19/2017 6:15 AM | |
Posts: 57 Rating: (0) |
sir we are commissioning new Siemens 6ra80 drive.as per operation manual startup procedure as per Quick commissioning DCM 6RA80Created by:lsierdsmaat: 1/6/2015 11:03 AM (1 Replies).I am not getting acess autorisation parameter p0003.i did the parameterization as per process and p3900 made=3, but after that p0010 no gatting 0.also drive tripping on F60056.please guide the same. |
12/19/2017 6:54 AM | |
Joined: 8/25/2006 Last visit: 5/3/2024 Posts: 2203 Rating: (277) |
r0949 in 6RA80 contains fault value as in 6Ra70. You can also look in r50047[0]. |
12/19/2017 7:10 AM | |
Posts: 57 Rating: (0) |
R 50047 showing 3 |
12/19/2017 7:17 AM | |
Joined: 8/25/2006 Last visit: 5/3/2024 Posts: 2203 Rating: (277) |
3: Rated field current of the motor not set (p50102) |
12/19/2017 7:50 AM | |
Joined: 8/25/2006 Last visit: 5/3/2024 Posts: 2203 Rating: (277) |
List Manual with fault description. Operating Instructions, look for comissioning steps in chapter 8. |
12/19/2017 9:08 AM | |
Posts: 57 Rating: (0) |
Sir i do not having acess to p2000 Please guide |
12/19/2017 9:46 AM | |
Posts: 57 Rating: (0) |
yes sir working from BOP20, not showing access p0003 and p2000. starting from r0000, then showing P0010. |
12/19/2017 9:54 AM | |
Joined: 8/25/2006 Last visit: 5/3/2024 Posts: 2203 Rating: (277) |
Look into Operating Instructions, chapter 9.2.2 how to change drive object and parameters from BOP20. |
12/19/2017 2:15 PM | |
Posts: 57 Rating: (0) |
Thank you sir P2000 set to 1800.drive trial taken.working ok |
12/20/2017 12:10 PM | |
Joined: 8/25/2006 Last visit: 5/3/2024 Posts: 2203 Rating: (277) |
Check p50115. |
12/20/2017 12:28 PM | |
Joined: 8/25/2006 Last visit: 5/3/2024 Posts: 2203 Rating: (277) |
Did you make required optimization runs? p50051=24, 25, 26? |
12/21/2017 6:47 AM | |
Posts: 57 Rating: (0) |
Yes sir.but arm voltage is not increasing above 290 |
Last edited by: Vishal Jakkani at: 12/21/2017 6:48:11 AM |
|