1/7/2018 6:57 PM | |
Posts: 5 Rating: (0) |
Iam new to DC drive commissioning, I want to run a 11kv dc motor with 6RA80 drive without tacho reference. Kindly suggest what are the required parameters to be enterednin drive to run the motor for testing purpose. ( Motor rated details entered in drive already and emf slecelxtion kept as P500083-3) Motor field resistance : 124 ohms Armature resistance : 0.5 ohms Kindly give some suggestions to run the motor.. Thankz ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 1/17/2018 1:04:09 PMNew subject after splitting |
|
1/18/2018 5:31 PM | |
Posts: 5 Rating: (0) |
Dear Sir, Motor rating is 11 KW and rated armature voltage is 440 V |
1/19/2018 5:24 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello K K raju, Please refer the attached sheets (Extracts from Siemens manual) about the quick commissioning of 6RA80 DC drive. In your case you need to set P50083 = 3 i.e. operation without tacho ( EMF closed loop) HTH. Attachment6RA80 quick commissioning without tacho.pdf (640 Downloads) |
This contribution was helpful to1 thankful Users |
1/21/2018 6:28 PM | |
Posts: 5 Rating: (0) |
Dear sir, Motors started smoothly after parameterization process. Thanku for your support. |
This contribution was helpful to2 thankful Users |