Hi Teens Once I tested a gateway fromSisco (I think that's the one you're using) and the problem was that Sisco should send several informations at the same time to Siprotec. The problem was on the OPC side, as the client could not write several informations at the same time. On Siprotec web site, on the right panel click Software -> IEC Browser. Install and execute this software. It's a IEC client which you can use to tests your commads. Here you'll see exactly which informations should be send to Siprotec. Also SBO can be done with IEC Browser. http://siemens.siprotec.de/download_neu/html_nav/ind_sw_e.htm |