Hi, You need some programming in the PLC where the CP 341 is installed. On the CP 341 you have to load a Modbus Master driver and you have to install the plug on the backside of the CP 341. See the handbook: SIMATIC S7-300/S7-400 Loadable Driver for Point-to-Point CPs: MODBUS protocol, RTU format, S7 is master And the Software: Loadable Driver "Modbus Master (RTU)"(You have to buy the Modbus RTU master package for the plug=licency) You need also to install the software for the PtP connections in the STEP7 manager: Download CD "CP340, CP341, CP440, CP441" Further you have to have a description of the Modbus slave which Registers and Coils the device have. |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|