I’m installing a 802D system on a simple 2 axis lathe. The system includes a 2axis Simodrive 611 unit 6SN1118-NH-0AA0 equipped with profibus DP3 card 6SN1114-ONBO1-0AA0, a power supply and 2 sets of PP 72/48 I/O cards. After installing the software, we set the MD11240 to 3 and the profibus addresses (12 for the 611 drive, 8 and 9 for the I/O units) but we got a problem in the profibus communication between the 802D system and the 611 simodrive: The drive is showing warning “A 832” “PROFIBUS not clock-synchronous with the master” and the 802D is showing 25202 alarm “X1 waiting for drive”- I tested the 611 simodrive using the Simocom software and it’s working fine - The PLC program and the I/O units are operating normally - The 802D system can see the drive in the “system / machine data” area, I can see and modify the parameter of the drive form the 802D keyboard, which proves that the profibus is working but I couldn’t solve this “clock synchronization” problem, I tried all the related parameters for the drive, but didn’t find any related information for the 802D side. |
5/7/2008 7:52 PM | |
Joined: 10/17/2007 Last visit: 3/14/2025 Posts: 4245 Rating:
|
Hi, did you check profibus cable to 611U, and make sure that the terminating resistors are only connected at the first and at the last stations(following the switch ON/OFF rule). ref. to commissioning manual 2.5 Connecting the Profibus give some feedback to Forum
|
Last edited by: nulizhang at: 5/7/2008 7:57 PMIf you like my comments please |
|
5/8/2008 5:19 AM | |
Posts: 5 Rating:
|
Yes, I've done this. in fact if the resistors are not set the profibus will not work at all. In my case it's working and retriving the Drive parameters but I have this alarm "25202" and the warning 832 on the drive that I couldn't reslove, it's related to "clock synchronization". |
5/8/2008 7:38 PM | |
Joined: 10/17/2007 Last visit: 3/14/2025 Posts: 4245 Rating:
|
I have no simple way to fix the problem. But if I were you I will try to test Simodrive 611 unit 6SN1118-?NH??-0AA0 equipped with profibus DP3 card 6SN1114-ONBO1-0AA0 togather with S7-300 PLC. to do this you need an S7 Cpu 315-2DP, STEP7 SIMATIC MANAGER. document ref. to SIMODRIVE 611U description offunction, Ch.5. if 611U controlled via profibus by CPU 315-2DP , and you still meet alarm A832. you may try to change DP3 or 2axis Simodrive 611 unit . you can also read help text from SIMOcomU for alarm 832. good luck! |