Hello, try setting 34050 = 1. The control will stop after the reference cam signal edge, then it will travel in reverse direction to exit the cam. Then it will stop and travel again towards the cam, looking for the firstencoder zero mark. Maybe thelink explains it better. AttachmentD:\802Dsl_FB_0311_en_en-US[1].pdf (119 Downloads) |
Last edited by: APC Tech Team at: 12/6/2012 2:34 PM |
|
12/6/2012 4:05 PM | |
Posts: 391 Rating:
|
It depends on the type of measuring system. If your encoder is incremental with zero track (ADI4 PIN 10 - 11) set 34200 = 1. |