Gadhavij I think, You should see PLC, NC status and alarms. If no alarms and NC/PLc run, it's not necessary download backup... When power fail occurs? |
1/6/2011 5:17 PM | |
Posts: 2964 Rating: (484)
|
Why are you loading the backup again and again ??? what is the error you get on the screen...... details required???? Regards, Ekalavya |
1/8/2011 5:31 PM | |
Posts: 2964 Rating: (484)
|
Hello.... Best way is to have DC UPS for protecting PCU 50 in 840DI machine... you don't have to load the backup. The backup is loaded from the MCI board if any interrrupt has happened.when you again switched ON it will load from this automatically Unless untill if you have not removed the MCI board..... check out the 840Di Manual in Docon WEB https://www.automation.siemens.com/doconweb/content.asp?item=2830&cd=sinumerik_simodrive_04_2010_e&scope=all Cheers..... Ekalavya |