11/7/2014 9:06 AM | |
Joined: 5/12/2006 Last visit: 9/20/2024 Posts: 22365 Rating: (3011)
|
Hello, on the Integrated the Bus Synchronization is alltime enabled. For external devices you must activate it during the projectiing in HWConfig. the configuration Steps are described in the SIMOTION Communication Manual. Regards Christoph |
Last edited by: ChristophD at: 11/7/2014 9:14 AM |
|
11/7/2014 9:54 AM | |
Joined: 4/10/2009 Last visit: 10/23/2023 Posts: 94 Rating: (0) |
Dear Expert Thanks for your reply. The HW configuration file is enclosed for your reference. Regards CRS
Attachmentsimotion d.zip (277 Downloads) |
11/7/2014 10:41 AM | |
Joined: 5/12/2006 Last visit: 9/20/2024 Posts: 22365 Rating: (3011)
|
Hi, i have make corrections : CU320-2 = Sync-Slave Update Time CU320-2 = 4 ms SendClock = 4ms IO-Cycle = Servo on CU320-2 Regards Christoph AttachmentD:\simotion d_c.zip (290 Downloads) |
11/7/2014 11:35 AM | |
Joined: 4/10/2009 Last visit: 10/23/2023 Posts: 94 Rating: (0) |
Dear Christ Thank a lot Regards CRS
|
4/27/2018 2:28 PM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (172) |
New question published by AutoGen_622152 is split to a separate thread with the subject Sinamics 120 - given fault 30025 and alarm 7805. Best regards |