Hello, The more you add slaves, the more the Profibus cycle time increases. The correct monitoriung times can be computed using the so called S7cotib.xls sheet. The firts sheet is to compute the needed time for the safety program when using S7-PLCs. The second sheet of the workbook is used to compute monitoring times. How to use the table is illustrated in this document: http://support.automation.siemens.com/WW/view/en/23926783 |
Best regards |
|