1/12/2012 3:32 AM | |
Joined: 9/27/2006 Last visit: 9/13/2024 Posts: 12282 Rating: (2683)
|
Hello sexdriver; First, look at the following extract from the ET 200M manual, specifically from the chapter on Interrupt, Error ans System messages. SIMATIC Distributed I/O device ET 200M Using this information, look at the present combination of LEDs and see if they match any condition in the table. The different diagnostics use a different setup of the differentmessage LEDs toqualify a specific origin of the fault. On the other hand, ifyou can access the Diagnostic buffer of the Profibus-DP master CPU (and you have inserted the required diagnostic OBs in your program, OB82, OB85, OB86, OB121, OB122...) then you can probably get a message explaining the source of the problem, as viewed from the CPU, over Profibus. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 1/12/2012 3:37 AM |
|
1/12/2012 4:02 AM | |
Joined: 10/7/2005 Last visit: 9/13/2024 Posts: 3020 Rating: (1054)
|
Hello SexDriver On the off chance that there is a typo in your part number and that you actually do have a -2Bxxx IM153-2, you may also findTHIS link interesting. I hope this helps |
Last edited by: fritz at: 1/12/2012 4:04 AMDaniel was faster with the same advise, truncated my entry to leave only the new additional info. Cheers |
|