10/27/2007 10:24 PM | |
Joined: 1/7/2006 Last visit: 11/17/2023 Posts: 2705 Rating: (315)
|
Dear Pandiani. The answers to your questions are below: 1. It is NO redundancy, the redundancy is for detecting a error in the Failsafe-I/O or in other parts of the CPU (e.g. Memory, EPROM, BESY, etc...). 2. From a output card (the P-DO) is put power on two different switches that are read-back to two different input cards. For the F-DO there are four cards involved, two output cards that give a plus and a minus and two input cards (P-DI)that are checking crossover if the output works well. Please download the handbooks of the AG S5-115F if you need more detailed information. SIMATICS5-115F Programmable Controller Manual Volume 1/2 SIMATIC S5-115F Programmable Controller Manual Volume 2/2 If you have any questions, then please ask them and I will try to answer them |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|