4/14/2016 10:21 AM | |
Joined: 8/3/2009 Last visit: 12/2/2024 Posts: 14294 Rating: (1784)
|
Hello Chris22222 No the Way in your Screenshot is "Tag Multiplexing" https://support.industry.siemens.com/cs/ww/en/view/21807421 I would not use this because you have a lot of disadvantages an you do not save Tags. The Adress Mutliplexing you can only use with adresses, so you can only use absolute Adressed Tags and no Optimized DB in PLC. If you go to the Adress of the Tag you can use insted of constants also Tags and so you can work with offsets. I would not work with Faceplates if you use Adress multiplexing. you can use for example one Screen for every Typical (area or Devicelike motor 1, Motor 2) and when you load the Screen (event) you can set the Offset Tag for the indirect adressing. or you use a Textlist for that. There are multible options to get it work. Bye Murof |
Last edited by: The Helping Hand at: 4/14/2016 11:07:05 AMMade the link clickable If this Information really helps, you could use the Rate function |
|
This contribution was helpful to1 thankful Users |