10/24/2010 3:46 PM | |
Joined: 9/27/2006 Last visit: 3/27/2025 Posts: 12344 Rating:
|
Hello me88; The purpose of the Y-Link is to connect normal Profibus-DP slaves to redundant Profibus-DP Masters that are required for the operation of a S7-400H system. Since "normal" DP slaves only have a single connection to Profibus, you need a module that will automatically switch the Profibus master line in case of redundant CPU failure. The Y-link uses 2 IM-153-2 and a Y-coupler on a "active" backplane for the S7-300 system. Each IM-153-2 is connected to a different Probibus line (connected to only one S7-400Hredundant master), and the Y-coupler is connected top the normal Profibus slave downstream. The small pdf below will show you details on the Y-Link, even though it speacks of IM 157 instea of IM 153-2é. It is an older manual, and modules have evolved slightly since then. But the principles work the same today. More details can be foung in the Industry mall link that follows, Look especially in the Product Information tab for the Y-Link: https://eb.automation.siemens.com/goos/catalog/Pages/ProductData.aspx?nodeID=9990035&catalogRegion=ww&language=en®ionUrl=%2f#activetab=order Hope this helps, Daniel Chartier AttachmentY_LINK_E.pdf (586 Downloads) |
This contribution was helpful to
2 thankful Users |
10/24/2010 4:54 PM | |
Posts: 947 Rating:
|
Hello me88 Small additional info: exist 3 modidfication Y-link: - old, based on IM157; - new 1, based on im153, used LA03 in MTBF; -new 2. used LA13 in MTBF. It's can send time to slave. All modely-Link can't send|receivemore 244 byte. |