I am new to WINCC Flexible How to acknowledge alarm by PLC or ACK key on OP77B? How to make alarm group. |
6/23/2008 2:34 PM | |
Joined: 4/24/2006 Last visit: 9/20/2024 Posts: 8742 Rating: (1168) |
Hello, Please have a look at following faq: http://support.automation.siemens.com/WW/view/en/19439876 Here are some manuals: http://support.automation.siemens.com/WW/view/en/18796010 Getting started first time user: http://support.automation.siemens.com/WW/view/en/18660846 Best regards, Wizard |
6/23/2008 3:10 PM | |
Joined: 5/13/2008 Last visit: 12/18/2019 Posts: 836 Rating: (71) |
To use the ACK-key on the panel, you have to give the operator thepossibility to see what kind of alarms he will quit and, of course, to select the right ones. Use the 'alarm view' (enhanced objects) for doing this, the template for screens is recommended here. To acknowledge all alarms, you should set the alarms to the same group. If one alarm of the group is acknowledged, all others of the same group are also acknowledged. Goto the alarm editor, right click to the Header line of the table and activate 'Group', to see the conerned groups of each message. Its also easier then to assign the messages to one group like doing it with copiing cells in excel. For acknowledge all alarms py PLC, you have to create additional tags (hint: the acknowledgment bit must be located in the same tag as the bit for the error alarm). Goto the alarm editor, right click to the Header line of the table and activate 'PLC ack tag' and 'PLC ackbit' , to see the ack tags of the PLC. See also chapter 2.4.2.4 of the manual: http://support.automation.siemens.com/WW/view/en/18797552 FAQ: http://support.automation.siemens.com/WW/view/en/19439876 |
mfG / Best regards |
|
6/26/2008 1:49 PM | |
Joined: 2/27/2007 Last visit: 3/30/2022 Posts: 79 Rating: (5) |
Thanks Wizard, Body Sorry for delayed reply Atharva |